I will add on to what
@ShadowFox has offered in no specific order of importance or relevance:
- Run Time: A UPS must be sized to the expected run time you want based on the load (wattage consumed) by the equipment. If you see very rare power outages say under 30 minutes. There are lots of selections to choose from but if you want X hours you are going to pay a lot more.
- Power: The utility supplies your home a pure sine wave output. Cheaper UPS use modified (simulated) sine wave vs pure sine wave. Depending upon the hardware many electronics operate just fine using PWM power. Whereas others require a pure sine wave output to run correctly. You can never go wrong using a pure sine wave UPS vs PWM. Many electronics will over heat, fault out, or run erratically when on PWM power.
- Online vs Line Interactive: Line interactive UPS offer loser (wider voltage) control vs On Line where the system uses double conversion. Depending upon the maker line interactive can swing from 8-15% in line voltage. Whereas a online offers 2-3% of line voltage similar to the utility hence why they are more expansive.
- Transfer Time: Line interactive UPS also have a momentary
cut in. Meaning the UPS will take time to transfer from utility to back up battery power. Again, depending upon brand and model this short delay can cause a system to freeze, reboot, shut down. In most cases generally speaking this isn't an issue but if in doubt a online UPS doesn't have this problem because its always online.
- Surge Protection: Line interactive UPS provide less protection with respect to surge protection vs their online counterparts. Because the dual transformers isolate the entire system from the grid.
Regardless of the above one thing you should always follow is the recommended battery replacement interval. Batteries are consumables and even sitting idle doing nothing will degrade. Depending upon the brand and type of cell used 5 years is the mean average for sealed cells. If the system is used often that life cycle can be 1-3 years of service life.
Lastly, always test and validate the UPS system can provide the expected run time once a year. In a Enterprise environment this is done once a month by literally pulling the plug from the outlet. Don't count on the software or some kind of internal timer indicating its good to go. This also high lights the importance of seeing if the UPS will come back on once utility power is back on line.
The distinction is NOT (IF) it will operate but (IF) it will turn back on (Last known state) while the battery is fully depleted. The market has dozens of UPS where the system will not turn back on until the battery is near full. That isn't helpful when you're not close to the UPS to remediate that problem!