I installed a system a while back where about 100 feet of cat5 cable had to be outside in the weather and in direct sunlight. I ran the cable in EMT, 1/2" metallic conduit, not waterproof. I know that unless one is using PVC conduit, glued together, the conduit will not be waterproof. A few years later we loose video and POE at the camera. I pulled in new cat5 and the customer is back in business. I ran other runs in EMT also, no problems. I finally stripped the outer insulation from the cable and noticed the orange wire (#2) felt a bit rough in the area where my TDR showed an open. I had other conductors open too. Stripping the orange wire I found the copper was falling apart. I didn't see anything obvious where the outer jacket was nicked but water got into the cat5 itself and eventually electrolysis did a job on the copper. As I said, EMT is not waterproof. I did not expect this to happen, it might happen again.
Has anyone else run into this problem? The cable was supplied by the customer, could it be cheap cable?
If this should happen again, what is a good solution? I've heard of PEX being used which can be made waterproof. Rigid conduit would work but is out of the question. I could skip the conduit and use direct burial.
or UV proof cat5?
Jim
Has anyone else run into this problem? The cable was supplied by the customer, could it be cheap cable?
If this should happen again, what is a good solution? I've heard of PEX being used which can be made waterproof. Rigid conduit would work but is out of the question. I could skip the conduit and use direct burial.
or UV proof cat5?