Recently purchased an ecobee smart thermostat and noticed my boiler was short cycling, staying on for 10 minutes or less every hour or so.
Investigating further, I noticed the heat is only turned on for .1 or 1/10 of a degree before it the thermostat sends an off-command and shuts down the heat.
By factory default the ecobee has the Heat Differential Temperature threshold setting set to .5 of a degree.
This means if the ecobee is set to 65 the heat will turn on at 64.5, which is a great feature I think, however it will shut off the heat at 64.6, only after .1 degree.
For factory defaults this doesn’t sound good for the boiler or any HVAC system and I wish we can also compensate for when we want it off since it’s not turning off at the set temp.
Currently not sure if this is by design or a bug, if someone can share a portion of their Heaton block.
Each cell is a 5 minute block. In the second pic, I have increased the Heat Differential Temperature threshold to a full degree from the .5 factory default and now the heat stays on for .6 of a degree. This is much better than the factory default but curious to see what others have.
In both cases the heat will turn off .5 of a degree from the desired temp but will run for .1 of a degree with Heat Differential Temperature set to .5, and will run for .5 of a degree if the Heat Differential Temperature is set to 1. The issue again is the factory defaults will only let the system run for .1 of a degree before turning off.
Investigating further, I noticed the heat is only turned on for .1 or 1/10 of a degree before it the thermostat sends an off-command and shuts down the heat.
By factory default the ecobee has the Heat Differential Temperature threshold setting set to .5 of a degree.
This means if the ecobee is set to 65 the heat will turn on at 64.5, which is a great feature I think, however it will shut off the heat at 64.6, only after .1 degree.
For factory defaults this doesn’t sound good for the boiler or any HVAC system and I wish we can also compensate for when we want it off since it’s not turning off at the set temp.
Currently not sure if this is by design or a bug, if someone can share a portion of their Heaton block.
Each cell is a 5 minute block. In the second pic, I have increased the Heat Differential Temperature threshold to a full degree from the .5 factory default and now the heat stays on for .6 of a degree. This is much better than the factory default but curious to see what others have.
In both cases the heat will turn off .5 of a degree from the desired temp but will run for .1 of a degree with Heat Differential Temperature set to .5, and will run for .5 of a degree if the Heat Differential Temperature is set to 1. The issue again is the factory defaults will only let the system run for .1 of a degree before turning off.